Following numerous joint site inspections with the client, architect, consultant and other relevant parties, we have reminded you several times that the access panel requires sufficient size for the maintenance of indoor units. So far, we have found that there are still some insufficiently sized access panels installed ,which will pose some difficulty for any future repairs. The condition of the access panels is listed below.
|
Item |
Location |
Condition |
|
1 |
Flat |
Sufficiently sized access panel for control box of A/C indoor unit has been provided |
|
2 |
Lobby |
Full access panel int corridor for front side of supply and return air of A/C unit has been provided. |
|
3 |
Dining room |
Insufficiently sized access panel for bottom side of return air of A/C unit has been provided. We would reiterate that the minimum size (300mm width x unit length) of access panel should be provided for future maintenance. |